CI867 as Modbus TCP slave
Could anybody give me some assistance in setting up a CI867 as a Modbus TCP slave?
The master will be a third party protocol converter to the CI867 as a slave.
Do I need to use the MBTCP Read function block if the 867 is a slave? How do the standard Modbus addresses of 40011 etc line up with the adresses in the CI867?
If anybody has an example I would be very grateful.
Answers
Greetings,
First of all you dont need to use MBTCPRead block, your system hehaves as slave to third party system. So you just need to identify global variables.
For more details please see attached power point file for configuring the CI867 as Slave.
Hope it helps you.
Add new comment