Freelance 2013 errror during download "Load Operation of Object 901 Failed Due to error ffff0104
I am recieving an error message when I try to "laod change object" while in control builder is in commissioning mode
This is error message pops up when it attempt to load any changes
"Load Operation of Object 901 Failed Due To Error ffff0104"
None of the changes are loaded
I deleted all the changes that was made and still the get the message
I did not try to load whole station as we only have one working conroller right now and I want to make sure it is not critical error.
Answers
Hello,
Which controller type it is ?
However, for any controller type memory redistribution is needed in such situation.
And that needs whole station download to load boot configuration to be loaded into controller.
Or even whole station download may temporarily solve the issue.
For memory redistribution get connect with your local/regional L3 support contact.
And for temporarily solution based on process and production schedule take a call.
Hope that helps.
Try to get the information what object it is that throws that error.
right click on the PS (in commissioning mode) that you want to download and select "Show selected objects" in the context menu that pops up
Should look like
Search for the object 901 in that list. Also some of your objects should have the state "dirty", look at them too. They differ from what is in the controller.
Maybe that gives you some idea what is wrong here.
by JuergenV Rank: 70 on 5/25/2018 3:20:04 AM | Like (0) | Report
Hi!
Are you sure you are using the project file you have used for the previous download?
Best regards
Jürgen
by Dieter Henkel
@Juergen: If it was not the same file you should get a "Version Error" and load changed objects would not be possible.
Add new comment