Freelance 2016 SP1: Incompatible DMS version error with AC900F
Hello,
I try to replace a new AC900F controller in my system. When I go online, the CBF notify "Incompatible DMS version" and I cannot load the CBF resource to this controller.
I'm using Freelance 2016 SP1 version; and the new AC900F controller have PR number = 06.01, FW = 0002. Please see the attachment for details.
What I have to do to resolve this problem?
Answers
Hello Hoang Van
If you haven't done it yet, try updating the controller firmware via the ABB Settings tool.
Best regards
Björn
You need to update controllers firmware, Might be unit you have replaced having older version or F2016 version FW.
To update you need to go to All programs > ABB > Freelance 2016 SP1 > Settings
There click on Controller firmware update > put IP address of controller if single then Ip address1 if redundant controller then both IP address
And press Load, will take 5 min or so and controller firmware should be updated.
Do not power off units while firmware is updating....
Then make whole station download from Freelance Engineering... It should allow to download now....
Hope that helps...
Add new comment