IR Smoke Detector Diagnostic Alarms
Hello Dear,
I am unable to figure out why diagnostic alarms like dirty optics and beam blocked are not working. Have missed something in configuration? Please advise.
Thanks & Regards,
RH
Answers
Hello,
It could be that your settings (NAMUR/device malfunction or underrange) are blocking the dirty optics/beam blocked signals below 3.8 or 3.6 mA. Try setting namur to false, and set the values to a settings below the 1 mA.
Hope this points you in the right direction.
Add new comment