Par_Conn entries for BDM missing in Control Properties aspect
I'm working on an application for a AC800 controller, where I'm planning to use the BDM to assign values to control module parameters.
But the Control Properties aspect only contains the _Init_Val entries for a parameter, no _Par_Conn entries.
Anyone that has a solution for how to get the _Par_Conn entries available in the Control Propertes aspect?
I'm using the Engineering Workplace, at a SV 5.0 SP2 RevC system.
Thanks in advance.
Best Regards
Rolf Lien
Voted best answer
Dear Rolf Lien,
You will get the Par_Conn parameters after the init_value parameters.. Check the attached screenshot..
Scroll down completely down in the list....
Answers
The solution to this is that the user has to be member of the 800xA Software Developers group.
E.g. this can be done from the command prompt with the command afwuhop ssd <your username>
Regards Rolf
Dear Rolflien,
I presumed that the User was already a member of Application Engineer Group. Anyways, good that u got the solution and thanks for posting it. People will make a note of this pre-requisite for BDM in future.
Thanks.