CI851 has question mark after upgrade from v4.1 to v5.1
Dear all, When open the project in compact control builder V5.1, CI851 has a question mark it can not download anyhow. Backup is taken from V4.1 of compact control builder. Please help me //
Answers
Have you upgraded firmware in CI851 and AC800M CPU?
Supported versions are listed in the release notes; please check that your combination of hardware and software are supported.
Too old hardware may allow download, but flag "Unsupported version" in hardware tree after download.
/Stefan
I already upgrade firmware, But problem not in Controller
Problem in Project, if I delete it then it is possible to download , but it needed.
I have attached a snap of it please see it.
//
I just solve the problem. Solution: 1.Download the firmware 5.0.2 to the controller. 2. Insert BasicHwlib 5.0.2 in libraries (Hardware) 3. Replace BasicHwlib 5.1.0 by BasicHwLib 5.0.2 in controller connected libraries
I just solve the problem.
Solution:
1.Download the firmware 5.0.2 to the controller.
2. Insert BasicHwlib 5.0.2 in libraries (Hardware)
3. Replace BasicHwlib 5.1.0 by BasicHwLib 5.0.2 in controller connected libraries
Add new comment