How to configure the HART DPV1 commands paraemeter table
HI
Please someone guide me in How to configure the DPV1 commands for HART Devices in Freelance. I know the commands as per the screenshots but don't know how to fill the table. Based on which calculation/reference the DPV1 parameter table has to be filled?.
Because I am not getting how the HartDS command length will increase?
I am trying configure but in OPC I am getting BAD for all parameters
Answers
Hi,
In reply to your coment to question, because AI815 is not supported for HART command, check image below from document ref. 3BDD012515 Engineering - Communication and Fieldbusses.pdf.
by Sumit Gargav
you are using AI/AO 895, S800 i/o?
by himanshu Rank: 249 on 6/30/2015 10:43:20 AM | Like (0) | Report
Yes I am using AI895 and transmitter is Rosemount_3051SMV_MultiVariable_Mass_Energy_Flow_1_HART_000026_0049_DD2_1_4_165_1_DTM".
Need to know whether it can be achieved for AI815 also ?
by himanshu Rank: 249 on 7/1/2015 8:42:35 PM | Like (0) | Report
With the Help of Jubin Abraham, we are getting the Data of Rosemount Instruments in SCADAVanatge through OPC.We used AI895 Module.
But the same is not coming when we are using AI815
Please tell how DPV1 Parameter table to be filled for AI815