Alarms are not getting updated in 800xA Alarmlist with safeguard (AC415)
We are not getting any alarm for 16 tags of a perticular AI card (DSAI130-S100IO) in alarm list. In facplate it is showing in acknowledged condition. Although We are getting alarm change in Control Connection, it is not getting updated anywhere else.
We are having 800xA version 4.1
Plz refer to attached snap.
Voted best answer
There are no limits enabled on the signal.
Enabled limits, eg HI_LIM1 would show as red strupe on bar graph, but it is not.
Additionally, LIM_TR must be set for alarm handling (refer to User's Guides, eg Event Treat section of the 800xA for Avant Master Configuration User's Guide).
/Stefan
Answers
Hello,Wat about for other tags is it alarm getting generated in xa if so look at the following:
1. Is it alarm is enabled in the block and downloaded to controller.
2. Is it upload is performed?