Hi,
The following P-Tree objects of Control Builder F are supported at present:
• Program Lists, Programs and Tasks
• Function Block Diagram
• Function Blocks
• Function Block Parameters
• Tags
• Variables
• Graphic Display
• Group Display
• Trend Display
• User Tasks
The following P-Tree objects of Control Builder F are not supported by Freelance BDM
• System Tasks
• Task lists
• All Hardware objects
• OPC and Gateway objects
• POOL
The BDM tool is available as a bonus component and can be used “as is”, free of charge, more info "BDM is recommended to run on Windows XP Professional SP3 orWindows 7 Professional/Enterprise SP1, (32-/64-bit) Operating System. Microsoft Excel versions supported are Excel 2007 SP3 (32-bit) and Excel 2010 SP1 (32-bit)"
If BDM is installed then It is simple to use right click on supported project tree object at end of context menu & you will get option to use BDM, from there you can browse through online help for detail use.
This is one of the reasons for which BDM was created. Duplication of whole FBD or PL is as easy as copying a row in Excel sheet - to be honest it is copying of a row that represents Your FBD/PL in BDM sheet structure.
For more info on how to use BDM refer to attached documentation.
Source: 2PAA105801R0201