PLC server service
Hello,
We install 800xa ver 5.1 rev E, with PLC connect, but we cant have the PLC server service , son generic network appears with errors,
Is there any way to activate PLC server service.
Answers
Hi,
In 800xA V5.1,it is possible to uninstall and reinstall PLC Connect from control panel. From control panel,for PLCconnect select Repair option and follow the onscreen instructions.
When prompted, provide the path to the PLCconnect setup file from the 800xA installation software package to reinstall with fresh files.
I generally use this procedure only if I am not able to resolve issues by simply reconfiguring the PLCconnect service providers or by disabling and then re-enabling the PLCconnect /softpoint server service providers.
Regards
Rahil
Hi,
If you have an exclusive server for PLC Connect, you also need to install PLC Connect in Aspect Server just for load PLC Connect Extension to system using configuration Wizard Tool. After that, you will be able to add "PLC Generic Control Network" Object.
If you have a single server, try to install PLC Connect again and add extension to your system.
Regards,
Cesar.