faceplate linking in Digivis 500
We have Digivis500 for our soot blowing application. The faceplates in system are not updating. The same tags which are configured in faceplates gets updated in logic (AC500) but not reflecting in faceplate. If we configure additional graphical point of faceplate tag, again it gets updated but not getting updated in faceplates.\
PL provide us some clues to check further.\
regards,
Answers
This question has not yet been answered.
by Dieter Henkel
When did the faceplates stop updating. Did you do a configuration change at that time?
Try to synchronize the item list and re-instantiate the tags. See if that helps.
by daoza Rank: 4287 on 4/27/2018 3:34:25 AM | Like (0) | Report
Faceplates stop updating after we replaced our server with new one as olad was having OS (WINXP SP3) issue. We liaded the backup in spare server and synchronized all tags. Whole scada is recovered but only faceplates are not updaying. Pl suggest further.