HI Soft controller error
Hi ,
I am getting an error while trying to download to HI soft controller in SV5.0 SP2 system. Please see the attachment for error .
Error 9159:ESD01 HW Build Version for controller is not supported by control builder or differs between dependent controllers.
I have 2 ESD Controller (AC800HI PM865) and 3 PCS (PM866).
I have this error only for the HI controllers , I do not get this error for the PCS controllers.
Any body experienced this before .
Thank you.
Voted best answer
Hi,
Is this the system not a fresh system?? Has it gone through multiple Control product installation?
Normally this error appears when your Soft controller version mismatch with the AC 800M connect version. If you re-install the soft controller and connect (if possible load connect and HI extension), this will be aorted out.
If possible show the connected Hardware librarues in your project (or controller).
Answers
Hi,
This error will come normally when you restore old system maintenance back-up to another system and try to download to the soft controller.
The systems installed and running at site might be upgraded latest version(s) of AC 800M Connect and soft controllers normally not since soft controllers wont be used in running system especially at site.
You can un-install the existing soft controller and version and install the soft controller again as per your AC 800M Connect version.
Hi,
This is because the version of soft controller you are using is not supported by the version of CBM. This has been a problem with some of the softcontroller build release with HI update software for corrections.
Try using a older version of softcontroller which come with Hi update.
Add new comment