how can i change control builder permission status
Greetings all,
we are using AC800M cotroller with 800xa system.i need to change some controller settings regarding time sync.i am getting controller access through cotrol builder but its limited permission i can only read the configuration not able to write so where i can enable write permission in 800xa system . i am not aware of that kindly guide me
Thank you all
Answers
Hi, Just check whether you are missing reservation of the controller hardware on CBM (4th icon on tool bar). Or share us the information about the dialog what you get during editing.
As far as I know you should not be restricted in downloading these kind of AC800M Controller settings. Nonetheless, you might want to check the following setup:
CBM -> Tools -> Setup -> Station -> Application Download
Check parameters
DisableDownLoad = false (Disable download from this station.)
ReauthenticateDL = false (The user has to make a new authentication at download.)
I hope this might help you.
CBM -> Tools -> Setup -> Station -> Application Download
Check parameters
DisableDownLoad = false (Disable download from this station.)
ReauthenticateDL = false (The user has to make a new authentication at download.)
I hope this might help you.
In addition to Previous answers, also please check whether your application is password protected. If it is Password protected, you have to overwrite it..After providing the password only, you can come out of Read-only mode.
Just Right Click on your Application-> Protection -> Properties ->Protection-> Check Override Password -> Enter Password..
Thanks
Add new comment