800xA faceplate apperance
Hello,
I'm looking for solution how to make left mouse double click cause opening faceplate (from graphic element - now it's configured as default - one click and faceplate occures)
another question is, if it is possible to make limitation for faceplate - I need to open maximum one faceplate of single TAG - now I've got no limitations and I can open as much as I want.
Answers
Hello,
Graphical elements are for the operator interpretations so whenever you single click the element refered aspect will be opened against that object.
what you will achieve with double clicking for opening the aspect?
If you want to give authentication give double authentication for the operation.
if it is possible to make limitation for faceplate?
Its possible to limit the number of faceplates to be opened through library str-default view class-faceplate system here aspect will be available to configure max noumber of windows by default its 0 means unlimited so you can enter the value & apply
Single left click will iterate aspect precedence list where faceplate is first in priority.
Read about aspect precedence in the user's guides.
Double click on alarm row activates alarm navigation. Action to call faceplate is possible (if not already standard). Read about alarm navigation in the ug:s. I doubt double click in regular graphics trigger alarm navigation.
With view class max number of concurrent windows is possible to limit. Pinning may override max, but is possible to disable by enabling "Replace pinned overlap" setting in user profile values.
double click is customer demand, still no solution how to do this
faceplate limitation - I need for example to open 9 faceplates (limit 10) and if I open the same faceplate (exact TAG) I need to replace one of 9 faceplates not to open 10th.