Sattline 2.2 system command MoveFile Debugstatus = 2
Hello, when using the system command MoveFile on Sattline 2.2, the returned Debugstatus is equal to 2, which is not documented in the manual.
Does anybody know what the meaning is ?
instruction:
MoveFile(FileName, FileNameDest, True, AsyncOperation1, StatusMove);
running system:
Sattline Workstation Maxi Version 2.2-41
Voted best answer
Hi
In manual SattLine Programming I found an explanation, Success with Warning =2.
See attached file with a ref to chapter, SattLine manuals, 2.3.
Why a warning I have no good idea. A limit of files set by SattLine/OS on a folder?
Have you checked Windows Log files to check for any errors/warnings?
If ypu transfer the file by copy/paste, do you get any messages.
By the way if you are running 2.2-41 I suppose we are talking about NT4 as MS OS.
I suggest you upgrade to latest version of SattLine 2.5 Windows 8.1.
Regards
Krister