What is the procedure for making communication between two PM573 processors as master and slave in modbus TCP/IP
For one of my project, i need to establish communication between two PM573-eth processors(AC 500) in modbus tcp/ip protocol (Master/Slave Configuration). Can anybody suggest me the procedure to establish it.
Voted best answer
Hello,
Set the Modbus TCP settings in both the PLC as shown in the attachment. Use the ETH_MOD_MAST block in the MASTER PLC to read and write the data from the SLAVE PLC.
Regards
Vijayaram.J