I can't set the date and time of my AC700F
Hi !
I try to set the time of the CPU of my AC700F. I've already seen the related questions on this forum. In the commisionning mode, I do "option --> set system time. But when I check the date of my AC700F, it's always 2013-01-01 00:00:00. And in Digivis, an alarm says "station system time not set".
What can I do ?
Answers
Greetings,
Similar question has been asked before. Please see below link for more details:
http://www402.abbext.com/Hello-I-Set-...
Hope ite helps you.
Thank you for your answer.
But I've alrealdy seen this topic. And even if I set the system time, the time in my AC700F is not correct... I don't know why...
Hello!
From your description it is not clear, whether this AC 700F is the only Control Station in your network and in your project. Try the following:
- I propose you make sure that only your Engineering PC (CBF) and the AC 700F are the single nodes on a network (connect both to an isolated switch).
- Make sure that the Engineering PC and the AC 700F are in the same subnet (IP identical except for the last part)!
- Check that the communication configuration in the CBF (Project/Network...) is correct.
- Set the IP configuration for the Enginheering PC explicitely in the Configure Tool, General Settings. Don't use Localhost or 127.0.0.1.
- Switch to commissioning mode and verify that you see the AC 700F as running in the P-Tree
Then set the time of the AC 700F.
Yes I exactly do what you say, and it's always the same result.
In an other forum, someone says that the IP adress if my CPU has to be 172.16.1.1 and for Control Builder and Digivis, the adresse has to be 172.16.1.17 and 18.
I will test.
Thanks
Simon
I solved my problem !
It was the sub network. I had to change it in 255.255.240.0. (I had 255.255.0.0)
Now the date is okay.
Thanks for your contributions !
Simon