AC400,Redimension,Transfer
Hi,
i needed to redimension a AC400 controller, but when i transfer the source files to the controller i get in all PC's the following error :
'PC PROGRAM NOT BUILT' and numerous other errors.
what is the problem exactly ?
Answers
Before you try to load source code, dimension database and PC area using DIMDB and DIMPC
Most likely, you forgot to dimension no of PC programs.
Im confused. Redimensioning an AC400 does not require source files. Where exactly are you getting this error from?
Redimensioning uses tables. Dump the total database with DUTDB. Dump the PC tables with DUTPT. Load them again with LOTDB and LOTPT and choose the option to redimension database and program table space as required. Once this is completed take the PC programs out of build mode and deblock them.
If you use a different procedure, like using source code, it takes much much longer and you will likely loose data eg start values, some pid settings etc.
Add new comment