Need "pm571-eth programming assistance"
"I need help connecting to and programming a pm 571-eth PLC.
I am using control builder plus V2.1.0 but that does not allow you to target the 571-eth plc and as such i am having a hard time programming it.
I have had limited success programming directly from CoDeSys V 2.3.9.46 which allows you to target a pm 571 PLC but not with a ethernet connection also. This allows me to upload a program directly via a TK503 serial to usb cable, however has a configuration fault because the ethernet connection is not included.
Can anyone give me some help on how to connect properly to the plc!"
How did you solve the problem?
Best Regards,
Rodrigo Fuchs
Answers
Let me know how you are doing ethernet setting in control bilder as well as in codesys.
if possible share screen shots.
Source:
Hi
the PM 571 Eth is programmable by Codesys and Sycon_net tool and it's belong the old series of ABB Cpu.
Find attached one example of configuration.
Other information in abb library
Hope this help you, lets us know about the results
Hello Rodrigo!
The solution is to add manually in Codesys the cpu, following this istruction and looking the attached images.
1)Open a new project in codesys and select one CPU PM571 (image 1)
2)After declaration of main POU, open PLC Configuration (image 2)
3)Select coupler --> internal none(slot) --> right click by mouse --> replace element -->and select PM5X1-ETH (image 3)
I hope this help you, let us know about the results