Log configuration for PLC connect signals ABB800xA
I am trying to creat log configuration aspect for signals which are connect to 800xA via PLC connect.
We have separate server for this PLC connect service on which 800xA is also installed.the data is recieving via OPC areva france.
When i creat LOG CONFIGURATION ascpect it dont connect.
Tell me the procedure to configure log configuration file successfully for getting PLC connect real values trends.
Voted best answer
Hello,
pre-requisites for log configuration.
1.Ensure basic history services is up and running.
2.Ensure history source aspect created at the control network/generic control network level for basic history.
3.create log template of your own in lib str->log templates
4.create log configuration aspect under object in control str (DON'T CREATE IN OBJ TYPE STR).
For more details refer IM manual