Does PM573-Eth with on CM597 support AC500 HA
Does anyone have proven example of AC500 HA working with PM573-Eth with one CI597 for panel communication.
For me with PM583-Eth HA is working fine not with PM573-Eth.
I read in one document in internet HA support from PM581 onwards..Is it correct?
I getting error message with PM573-Eth "There is no ethernet link between PM1 and PM2 in AC500 HA system"
Already check the redundancy cable and both PLC's are running fine.
Any suggestion are appreciable.
Answers
Hi,
HA is possible with the both PLC PM583 & PM573.
In ABB HA manual they mention basic requirement of HA :
Two AC500 CPUs are required as central hardware components. Each CPU must be equipped with an integrated Ethernet port (or Ethernet Communication Module) and a connection for a CS31 master system.
Can you attach your PM573 system architecture here?