Maximum # IOs on AC700F
How many IOs can I connect to an AC700F?
256 IO locally + ????? over Profibus???
Voted best answer
Hi,
max 256 binary I/O locally. The sum of local I/Os and Profibus I/Os should be not more than 300 I/Os. The max. limit of Profibus I/O depends on baud rate, slave size, DPV1 messages, CPU load etc. Therefore I would recommend a detailled calculation by Freelance Wizard's DigiSize tool for larger applications
Answers
Hi
AC700F can have up to 256 maximum IO. It can be either 256 IO locally or remote via profibus. Or (mixture of both).