Redundancy Configuration with CI868 (IEC61850)
I'd like to make redundancy configuration with CI868 (IEC61850).
I already knew that module redundancy is impossible but, application redundancy is possible about CI868.
So, I'd like to get the manual about redundancy configuration with CI868.
and if you have it, Could you share it with me??
Thanks.
Voted best answer
Hello,
You are right that CI868 supports application redundancy. for that you have to generate the same configuration under 2 different CI868 and choose from the application from which CI868 to read data based on the unit status of CI868.
Attached is the manual that can help you.
Thanks.
CI868 does not support module redundancy however you can have application redundancy.For application redundancy you have to generate the same configuration under two different physical CI868 and choose from the application from which CI868 to read data based on the unit status of CI868
Add new comment