800XA 5.1 rev C problem
recently I install, 800XA 5.1 rev C, and i have one problem to use search function,
in control builder M
when try to search in offline mode it does not work, does not show any message of error,
If i try to search in online mode it works, but when try to go the reference appears a error : this reference is in other project and close the actual project to go there.
but we really have just one project.
Voted best answer
This is a known issue and there is a Product bulletin and the Product issue number is 800xACON-MS-5102-001.
You can access the PB in the link http://abblibrary.abb.com/global/scot/scot387.nsf/veritydisplay/fe04915093fdeda
ac1257b47002be55a/$file/3BSE047421D0131_-_en_AC_800M_Control_Builder_5.1.0-2__I
ssues_with_Search___Navigation.pdf
Extracts from the PB.
Corrective Action or Resolution
Workaround Online mode search
Don’t use the menu options “Go To…” or double-click on the items in the “References”pane. The workaround is to manually locate the object that is shown in “References” pane
or use only Search in offline mode.
Workaround Offline mode search
Change “Filter Result” to a different value or just reselect “(no filter)”. This will show the search result and it is possible to navigate from the reference pane.
Correction
These problems will be corrected 5.1 RU3 (5.1.0-3) for AC 800M Control Software which will be part of System Version 5.1 Rev D.
Source:
Answers
Let me know if this helps
–Offline and Online searches gave the same result prior to version 5.0SP2. Online searches were modified in version 5.0SP2 to be so called iterative searches (formerly known as deep searches).