Why the error: Error in checksum 0A086CDE
I have a PM864AK01 CPU, the firmware upgrade is work correctly but when i try set up the IP adress, i can´t configure that. I connect the hyperterminal with Putty software and at the restart of the cpu Putty show "Error in checksum 0A086CDE" such as the attached file. Can someone tell me what the error is?
The CPU doesn´t have a CF card. I'm thinking of buying a CF Card, maybe that's the mistake.
I thank you in advance for your help
Voted best answer
Hello,
regarding: I connect the hyperterminal with Putty software and at the restart of the cpu Putty show "Error in checksum 0A086CDE" such as the attached file.
During IP setting: Only primary IP CN1 will be set from the serial cable/putty serial port with port settings (by keeping backup controller OFF, In your case its K01 single controller) Once IP set restart the controller
You can confirm the set IP in controller log.
Here you have restarted the controller means hope IP already set serial connection between CPU and PC disconnected its known when restarts.
Check the logs
Answers
No CF card found is a normal message if there is no CF card.
Can you retrieve the controller log ?
The checkum error implies that your firmware did not upgrade correctly.
Add new comment