Need to restart Softpoint server to get screens to update
Hello
I have some AC800M connected to 800xA with PLC Connect. After I have added an object and made a deploy the update of the screen stops. To get it starting I need to disable the Softpoint server running the redundandt starts and then enable the disabled server again.
When I do this a number of ghoast alarms that is not possible to acknowledge appears.
This is pretty anyoing, do anyone had this problem and know a solution?
Running 800xA v5.0.0
Voted best answer
This issue is reported to be fixed in SV 5.0 SP2 Rev D.
Comm server hangs during deploy: 800xAPLC-CN-5020-014 is the product issue number.
Please get in touch with the local L3 supportline to check is there is a Temporary fix available in the current version.
Add new comment