800XA 6.0.3 connectivity server pu410 RTA board configuration
Hello support,
800xa 6.0.3 has been installed on the ASCS - server with windows server 2016 operating system, AC450 controller has been used in this configuration. under control structure when we try to open RTA board configuration for modification of EVENTS & RTA board backup. getting error msg " online builder not found"
Answers
is it SV6.0.3? then Windows server 2016 is not supported for this version only Windows server 2012 R2 standard supported as server
is CBA properly installed or properly configured using SI? ie Advant Master connectivity services are properly configured through allocate functions?
You have to be logged on to the connectivity server where the RTA board and on line builder are installed. You cannot do this from another client.
As mentioned you need 6.0.3.1 for Server 2016 LTSC support.
Add new comment