Hi,
I have two 800xA system (diffrent SID's). I will name them "Syst1" and "Syst2" below.
System info:
2 x 800xA system.
2 x AC450 (node 15 and 16)
2 x PU410 RTA, one for each system.
Both system are connected to same MB300 network (net 12). On my network I have two AC450 controllers. Syst1 are the main system for the MB300 network and for the AC450 nodes with some local and remote I/O underneath.
Question: It is possible to configure same controllers to the other system (Syst2). Two system that subscribe and manage on data from same controllers and same object in the controller? I whant to connect some of my Motcon object to the HMI in Syst2.
Thanks in advance!
Answers
Yes that's possible it's not much different that connecting two Unix OS to a controller. The only thing is that it's possible to overload an Advant master system with a modern HMI / historian / OPC client (mainly the historian OPC). You have consider the subscription rates (1,3,9 seconds) when you use Historians and opc clients.