View Only Control Builder Access
Hi,
Is there a way to only allow very basic control builder functionality to users? Basically, I would only like to allow certain users to be online with the controllers to view logic live, but I don't want any ability to reserve, make changes, etc. until they have some sort of formal internal training.
Thanks in advance for any tips/suggestions.
We are using 800xA 5.1 FP4 revE, Control Builder M.
Thanks,
Mike
Answers
Hi,
You can password protect your applications,CM Types, FBD types, diagram types and data types.
Refer to manual(Page 158 onwards):
Functionality is also available in SV 5.1.
Hope this will serve your purpose.
Hi,you can disable the download option for Application to controller from a specific station in which the user is always accesing.Follow the below steps to do this.
Open CBM-->Goto Tools-->Setup-->Station-->Application Download-->Disable the Download option.See the attached Image.By this option they are allowed to go online mode only.Not able to download from the Particular station.
And Already Dash has mentioned that By protecting password for the application users cannot allowed to change the logic.
Add new comment