I am not getting "System Setup" under "system configuration console" (800xA version 6.0.3)
I have Maintance backup (Full backup) of 800xA 6.0.3 version, when i am restoring the maintance backup it has loaded sucessfully, System is "UP". I am able to open Engineering Worplace aslo.
But only problem i face is i am not getting "system Setup" under "system configuration console"
Kindly help me to get the solution.
Answers
Hello,
I assume you have executed System Extension Maintenance in Configuration Wizard ?
If not, do it.
The problem is that you have different 800xA Base version in the original compared to where you restore. Probably 6.0.3.1 ?
/Ronny
Export and save the System Configuration and System Configuration State aspects
from original node(the node from which you take the maintenance backup) Admin Structure > Administrative Objects > Domains > <SystemName>,Domain
The following shall be done in the restoration node
Import the System Configuration and System Configuration State aspects.collected from original node
The aspects are to be imported to the below path:Admin Structure > Administrative Objects > Domains > <SystemName>,Domain
Configure System task is intentionally hidden during an update.
Use log files to find out why update does not run to completion.
There are known pitfalls, eg when opening Configure System from concurrent node during critical phases of an update.
File official support case to obtain professional support.
You should follow separate procedure to do 6.0-x backup restore or for upgrade from 5.0 X or 5.1 –X version to 800xA 6.0-x. The procedure is mentioned in installation and upgrade manual.
2PAA111694-600_F_en_System_800xA_5.1_to_6.0_Upgrade.pdf -> Preparing the 800xA 6.0 system (Offline).
Add new comment