Aspect cum connectivity redundant server not configured with History server .
Hi ,
i have 800xa SV-6.0.3.1.
system configuration is 2 Aspect cum connectivity redundent server and 1 no History server.
i have configured 1 no Aspect cum redundant server earlier and forgot to add 2nd one withHistory server now when I am configuring the 2nd ASCS Server as redndant server for History services after installation the RTDB folder is not creating in ASCS redundant server there 1 folder is getting created by the name History_temp i have attced the photo for the same.
now how i have to slove the issue.
Answers
Hi,
I would advice you to thoroughly read the following manuals and also search AKS forum for topics on 800xA History.
2PAA107280-600_E_en_800xA_History_6.0_Installation
2PAA107563-600_C_en_800xA_History_6.0_Administration_and_Configuration
As per the installation manual, the History Server role must not be combined with any other server roles.This means that, when assigning node functions via SCC, Connectivity servers must be assigned with Data Collector Node function and only your History server node must be assigned with 800xA History Server Non-Redundant function.
Read the description in the below image.
Regards
Rahil
Add new comment