Hi,
I am trying to restore the Backup of 5.0 system in 5.0 system, but I am facing below attached error.
Error Message is " More than one node is mapped to the same node"
But the installed system is not having any system as running.
Kindly help us to resolve this issue.
In the same system i tried to restore some other 5.0 system bbackup, which is sucessful.
Answers
Hi,
If the restore runs in a different system than the backup was made in, a primary node
in the backup system must be remapped to the node your are running the restore on.
You remap a node by right-clicking the node in the restored system, and changing
the node name.
Below Image for your reference:
You have two nodes with the same name (name OS-6) in the backup you try to restore, correct this in Node Administration Structure on the original system and then make a new backup.
by Dash
I assume you have already remapped your primary node in backup to the node you are restoring this Backup.