PLC Connect Error on some Aspects "The specified View * is not allowed
I can't figure out why this happens. It was working!
Uninstalling PLC connect and reinstalling PLC Connect seems to temporary solve the issue. I don't see me doing this on a productive system.
SV is 5.1 Rev D FP4, PLC Connect 5.1.0-4
Shall the PLC Connect VB Graphics Extension be installed ?
Answers
The attached picture indicates that PLC Connect is not installed on the node you work on, make sure to have the right version installed.
You can also look at System Extension aspect in Admin Structure to verify that the correct PLC Connect is installed (and loaded).
VB Extension is not needed unless you use VB displays instead of PG2.