AI801 peaks on three channels, no errors in unit status
Settings (Hardware) is 4-20mA on all channels and process instrument says 7 mA on the channels peaking to the value set under Properties tab (Hardware).
Tried to move one of the signals to another IO-unit nut the error followed.
Any suggestions?
Answers
And of course, after struggling with this problem for days and finally posted this question, the problem was solved by changing the scaling. Which I thought was correct in the first place since this has been working fine for years...
Someone or something, somehow at some point obviously has changed the scaling (min-max) to some stupid values!
Seems to work as expected now.
by Dash
didn't get the part "process instrument says 7 mA on the channels peaking to the value set under Properties tab "
Kindly elaborate..
by hobe Rank: 2820 on 3/7/2018 6:26:18 AM | Like (0) | Report
7mA when messuered the wire with fluke clamp meter 771 (mA).
by kstoilov
Your question is not clear - please explain better.
What do you mean pick to the value set under...
by hobe Rank: 2820 on 3/7/2018 6:32:32 AM | Like (0) | Report
...Hardware config, AI801 Settings tab.
Add new comment