I have a AC450 (PM510) and when entering the Online Builder on a given node the following message appears:
Error:"Failed to open device file "\\.\ccprinin8". Errno = "0"" Has anyone ever had this problem? I would like help, please ..
Answers
Please search for status report "3BDS013843 - PU516 driver problem after installation of ONB 3.0/2" it gives a sollution for this problem. It has something to do with incorrect RTA board driver installation.
- Verify that the PU410 device driver is properly loaded (check in Device Manager).
- A number of WUDFHost.exe shall be visible in Task Manager.
- EBSetup shall indicate "PU410" as in the image below.
- It is not required, but we do recommend configuring RNRP between host computer and PU410 for supervision of connection.
For further assistance, please file a support case with your regional ABB contact center.
by Stefan Stromqvist
What version of Control Builder A do you use? What type of engineering board do you use (PU516, PU515, PU410, ...)?
by DouglasMairink Rank: 4677 on 3/7/2018 6:05:09 AM | Like (0) | Report
Hi Stefan,
I use the version 1.4/0 Control Builder A and a PM410.