Going online with multiple PLC's in Automation Builder
Hello,
we are working on a project in Automation Builder with multiple PLC's. This is working fine, but is seems impossible to go online with other PLC's then the upper PLC in Automation Builder. Going online in Automation Builder instead of codesys can be usefull for error messages from the cpu etc. If we select the third or the fourth PLC and we click online then every time the first PLC goes online and not the third or the fourth.
We know the existance of the download manager, but this is only usefull for application downloads and firmware updates.
we are working on a project in Automation Builder with multiple PLC's. This is working fine, but is seems impossible to go online with other PLC's then the upper PLC in Automation Builder. Going online in Automation Builder instead of codesys can be usefull for error messages from the cpu etc. If we select the third or the fourth PLC and we click online then every time the first PLC goes online and not the third or the fourth.
We know the existance of the download manager, but this is only usefull for application downloads and firmware updates.
Voted best answer
Expand the tree of the PLC you would like to go online with and right click the gear --> login
Answers
Hi Maurice
this is a very intersting question, are you using the last version of AB?
Probably is not possible to open more session of Codesys at the same time in the same project, but really I not have tested before...
Let's see if other colleagues have already had this experience..
I made some screenshots to visualize my problem. I am working with Automation Builder version 2.0.4.4270 standard edition.
Add new comment