800xa with ac450/mp200 using pu515a
Hi.
I had been looking your profile and i saw that you have experience with ac400 controllers. Probably you can help me in this issue.
I have one station( singglenode) with 800xa v4.1 . and i tried to instal the control builder A on the same singglenode. I already installed the RTABOARD(PU515A) and already configurated.
In control structure->RTA board_> ac 400 conecct my RTA board is running and have a green singal beside the net node(in case 11,80). I created the MP200 and AC 450 on the same level of the RTAboard, but, when i try to connect with he on line builder on the node 11,11(mp200), the following message apears''UNKNOW TARGET... ''
I did all that i know, but cannot comunicate with he controller.
the dip-switch are configurated correctly.
The trancievers are blinking like already having a comunication between they
Can you help me in this question?
thanks
Yuri Durski
Brasil
Voted best answer
I assume you open online builder from control builder a not from within 800xa right?
When you install control builder A did you choose to share the rta board with 800xA? Do the controllers show up in 800xA under net node status display?
Answers
Like mentioned already verify if controllers are strapped for MB300E(xtended).
You can also change to 300E on RTAB (MDB NETWL9) and see if nodes appear.
Any 17,8 (hardware fault) system messages, eg missing heartbeat on transceivers?
Dear Yuri Dursi,
You can access the nodes from Application Builder(Control Builder) only. Ensure both(RTA board & Controllers in the network) are on same protocol, either all in MB300 or all in MB300_E only.
CS513/CI547 of MP200 and AC450 you can check the DIP Switch strapping for protocal - for a change you need to restart the controller.
in RTA board, access it via online builder through 800xA and open MDB NETWL9(may vary depending on the case..NETWL1) and check for the same protocol you set for controllers. If you do a change here, take a RTA board backup after terminate the session and wither restart the machine or restart the RTA borad. See you should get all the nodes available in the network.
If you need any further help you can reach me out on Lync or email(balagangadhar.y@in.abb.com).
All the best.
Balu.
Hi
Did your problem get resolved ?
If not, please share a snap-short of your control structure where you have created MP200 & AC450 nodes and AC400 CS Communication display Aspect screenshot.
Regards.
D. Das
I was working on this case and I found the problem with your help . I did some things , as mentioned above, in the answers.
I changed two things :
1-> the MP200 's bus driver DSCS 150 to 140 DCSC , restart the MP200 .
2- checked the dip- switches and rtaboard setting in ' ' MDB NETWL9 " .
After that, I had looked at the status of the controller in the control structure and RTAB and MP200 are green , so I tried to call the node 11.11 with ONB and surprise, I had been connected to the node and communications are good.
Thank you for all you did for me and all the tips .
Now my singglenode is functional and can do a lot of simulations to my process .
Thank you so much . Yuri Durski