Log data tag dump file creation
I am using 800 XA.
We are having an issue that some new tags to be added for data logging. But tag limit for data logging is already reached. 1500/1500.
I want to optimize the tags.
So can I take dump file for logged tags in excel, so that I will scrutinize the unwanted tags for logging.
Answers
Hi shunkahari
I suggest that you use Bulk Data Manager (BDM) to fetch objects from Control Structure that has a Log Configuration aspect. Bulk Data Manager (BDM) is described in 3BDS011223-510 - System 800xA Engineering 5.1 - Engineering Studio
I hope this will help you.
BR Carsten
I suggest that you use Bulk Data Manager (BDM) to fetch objects from Control Structure that has a Log Configuration aspect. Bulk Data Manager (BDM) is described in 3BDS011223-510 - System 800xA Engineering 5.1 - Engineering Studio
I hope this will help you.
BR Carsten
Hi,
In IM run this command in cmd prompt
C:\> hsdbmaint -report > report.txt
It will take some time to generate, depends on Log Configuration.
Add new comment