We just installed a new AC 800M (PM866) controller in our plant. Everything looks good untill I try to add an application. I make a download, and I get the red X's through everything on the HSI display. I have no hardware errors, and the program is running in the controller. If I run name uploader I get OPC quality "Bad(not connected)" for everything. All of the control builder settings for the controller (IP address Ethernet port 1 ect.) are correct as far as I can tell. Has anyone ever seen this before? Thanks in advance for any help.
Voted best answer
Did you add the controller ip adress in the opc server?
Answers
To add a new controllers into the existing system you have to follow below mentioned points.
1- Check the new ip address, by ping into the control structure.
2- Configure the controllers ip by using the new allocated ip addresses.
3- Connect the new controllers into the N/W ring.
4- Check the RNRP should detect the new controller-IP's.
5- Add the new controller IP's in OPC controllers.
6- Check the Node administrator for new node services info.
7- Define the new node and secondary IP address in the controll builder and down load the program.
8- Check the RNRP status, it should be normal.
9- Create control structure and upload the new tags from your new controller.