Change the time stamp for a CSWI logical node
I'm using a ABB REF630 relay, that has time synch via a SNTP server.
The time of the relay is correct, but the time stamp i get from the CSWI node, when operating fx the CB seems to be the UTC time and not the local time on the relay and the server.
Do anybody know why the time stamp isn't the same as the relay time, and how to fix the problem?
Voted best answer
Yes, this is for all the CSWI\Pos\t in the system.
I have attached the CID file for one of the relays. The configurations of the relays are nearly the same.
Answers
Hi,
Thisi happening to only CSWI LN or for all the LN on REF630 relay.
Can you please send us the CID file ?
I am answering based on my expereince.
My understanding is your IEC61850 client is running on the 800xa Server, From there you are monitoring and controlling the IED's . In 800xa >Communication engineering tool (CET)is collecting the Data from IED's and it is sending the data to 800xa using services.
CET is having SNTP client>you should configure SNTP client in the CET tool, Means you have to mention the SNTP server IP address. In your case i think CET sntp client is not linked to the SNTP server where the REF630 relay is linked, It may be having the UTC time by default, that may be a reason for the UTC time.
Hi,
I have imported te CIDfile and found that Time setting is not configured.Please find the attached screenshot and update the field as per your country time difference.