800xA Advant Master Connectivity Servers Redundancy
Hi. I have an 800xA 6.0.1 installation with one Advant Master connectivity server (using a PU410 in a MB300 Network named 'TITAN Net 1') . I have added a second server with a new PU410. Then i tried to configure redundancy for the second server. The procedure finished without errors but (see the attachements) now i have a new MB300 Network named 'NETWORK 1' with the new RTA board.
Answers
Sounds like something we should investigate at Supportline.
Please have a case escalated to the SE L3 Support Center.
Ask your regional ABB Support for assistance with creating a case.
The MB300 Network created while installation of one Advant Master connectivity server in 6.0.1 also would have been NETWORK 1 which would have been changed to TITAN Net 1 manually.
This by default it takes the name as Network "Network group number" i supppose.
Did you provide the Network group number as '1'?
by Basappa G Rank: 46 on 2/6/2018 5:09:29 AM | Like (0) | Report
kindly share System Configuration Console (SCC) Screen Shots
by elbar Rank: 186 on 2/6/2018 5:15:45 AM | Like (0) | Report
Unfortunately i don't have any screenshots.
by Basappa G Rank: 46 on 2/6/2018 5:21:29 AM | Like (0) | Report
This functionality is available in the Configure System task in the SCC under the
'System Setup' folder.
• Go to System nodes tab, and select a System node in the list.
• Use the Make redundant command.
This will open a dialog for configuring redundancy.
hope You fowled above procedure to configure redundancy
by elbar Rank: 186 on 2/6/2018 5:25:31 AM | Like (0) | Report
Yes. I did follow the above procedure and the procedure finished without errors. I don't know if the problem has to do with the fact that i renamed the default MB300 network name from 'NETWORK 1' to 'TITAN Net 1' ?