Dear ABB,
I have DCS 800F with 900 RIO field mounted modules, we need to change the RIO field cabinet to be adjacent to indoor DCS cabinet, we need also to involve the reboiler or Burner managment system in DCS signals .
note that we have existing natural Gas dehydration TEG unit being in rehabilitation activities.The existing reboiler signal and flame detectors have separate fiel local control panel.
please can you recommend the type of safeguard RIO moduled with the requirements to revamp.
thnx
Wissam A. Hameed
Basrah Gas Co.
Answers
Dear Wissam,
Could you please give more details about operator station and dcs interface.
Also you need to give more details about the safeguard system if you are using (800f) is not a safeguard plc.
You can use high integrity, safeguard or plant gaurd according to your budget and existing system