Not able to configure redundant PM866 with BC820
While configuring redundant PM866 with BC820 , after connecting the TK857 cable between the Controller and the BC820 module the Controllers (both Primary and Secondary) is going to Fault.
Answers
What's printed to the controller logs?
the RCU Control link cable needs to be configured correctly according to the color code.
Add new comment