AC-700F CPU Error
Hi,
The AC700F is displayed ERROR on this screen.
This controllor is configured with Freelance 2016 SP1.
the log of diagnostic is like as following:
48 .... CPU fault 30000203 at 0x002417DC 25.12.17 12:08:52.929
How I can know why we have this fault of CPU?
Thanks
Voted best answer
Hello frlulu,
it is hard to analyze a fault based on a single entry in the error log. Usually the context is very important.
The code stand for an alignment error, which means that a data structure is not aligned (to even byte counts) correctly. This can happen for example, when memory size of a data structure calculated during runtime exceeds the reserved memory for that structure.
Install the RollUp 2 for Freelance 2016SP1. Don't forget to load the controller firmware with the setup.
Hope that helps.