trend display @ graphic display
Dear rob
in our plant we are using the abb800xa 5.0 with ac450 controllers
i would like to add trend on the graphic display continously. i tried with advant objecttrim aspect from graphic pimitives.when ever i change the screen and revert back to original screen all the trends start updating with preset time
but i need permanent trend display on the screen
please suggest
with regards
veko
Voted best answer
Hi,
use an Aspect View Wrapper in your graphic display (can be found in "Special" toolbox) and set the ViewReference to the desired Trend Display.
Answers
Hello,
Are you logging your properties in Log Configuration-aspects ?
Otherwise I think it will be difficult to get what you want.
/Ronny
Add new comment