how to upload MMCX (RTYPE 36) to 800xA system
Dear sirs,
Does any body having face with our problem and any solution available ?
We have one system upgrade projects which only using 800xA SV5.1 to replace the OS500 Unix Stations, all AC450 / AC410 controllers are remained, the connectivity is for advant master.
Normally we use VB tools of 800xA to convert Unix Station Graphic files into VB displays, then we use VB graphics converter to PG2 ones.
We find one kind of MMCX ( RTYPE 36) display elements failure during the converting, because they were not belonged to the standard types in the unix station library, And now our our advant master objects of 800xA system also miss these aspects.
We try to use "MB300 User RefType object type " or "MMCX1" under the objective structure to creat its function properites, parameters and graphic elements, but we cannot upload these objects from the AC450 controllers, we can do nothing now.
MMCX4 MMCX
:NAME 290HS0421B
:DESCR LP STEAM TO PM1
:RTYPE 36
:IPARMAX 0
:RRESMAX 105.000
:IRESMAX 0
:INTWA 1
:REALAMAX 200.000
:REALBMAX 1.000000E-01
:REALCMAX 50.000
:ORD_BLK B0111 0100 0000 0011
:I1_EVBLK B1111 1100 1000 0000
:I2_EVBLK B1100 0000 1111 1111
:O_EVBLK B1111 1111 0011 0111
:AL_BLK 0
:PR_BLK 0
:ORD_TR 8
:I1_TR 10
:I2_TR 12
:A_TYPE 1
:PROC_SEC 8
:I2_12TXT 0422/0421 not OPN
:I2_15TXT BLK INTERL ACT.
Hope to get some support from here. Many thanks in advance
B/R Juan Yu
Voted best answer
MMCX with RTYPE=36 is a Pulp and Paper solution developed by Sinagapore Projects group originaly for a Paper Mill in Australia. The type circuits then became faily standard in Paper Mill AC450 applications used elsewhere. If I recall correctly, the MMCX is a variable speed drive.
The Object is being uploaded correctly, but you are missing a library for the RTYPE 36 variant, so the uploader cannot create all of the required aspects for this object.
You should talk to the DCS projects group in Singapore about this object. There is a standard solution available. If you cannot get the files that you need from them, then I can probably put you in contact with the original customer that uses MMCX type 36. They already upgraded to 800xA several years ago and do have a solution for this.
Answers
when upload all DB to the system, other types of objects are found under control structure, but only this MMCX (RTYPE 36) cannot be seen anywhere.
your case: you can see the object (like 60SN01Q0) under MB300 MMCX1,