No OPC connection from a third party server (2016) to ABB connectivity server (2008)
I tried to make an opc connection from a thirdparty opc-client which runs on windows 2016 server to a 800xA connectivity server which runs on windows 2008 server.
I setup the right DCom settings, with a dedicated user for the AfwDSOpcSurrogate.
I got an error on the 2016 server that the RuntimeBroker doesnot have the right permissions, but windows does not allow to change this?
When the thirdpart opc-client is running on a windows 2008 server the opc connection is running good.
Answers
> "I setup the right DCom settings,"
No, you probably didnt. DCOM settings are a PITA to get right. Use this to verify ....
https://advosol.com/product/22/opc-se...
The DCom settings where right.
The only thing is that OPC Core Components Redistributable version 3.0 had to be installed on the third party 2016 server, and not version 2.0