Modbus, AC800M, PM860.
Hello, you answered my question regarding MODBUS RTU communication with ac800m pm860 controller with some pictures. I am having trouble viewing the pictures because of the resolution, do you have those pictures with more zoom or higher resolution?
Here is the link http://www402.abbext.com/ViewQuestion...
Best regards
Håkon Kindsbækken
Voted best answer
Very important is also following:
In CP853 folder (or com parameters folder) in CB - Set Poll Time = 0 in hardware configuration, settings for Modbus. This cancel waiting of FC8 respond from the slave, which is not supported by all vendors, and gives valid status of MBConnect immediatelly.
Add new comment