Modbus Variables Freezing - CI867 - Error Message: "Fault Comm WD Time"
Dear,
I have some Modbus Variables frozen after the erroe messagem "Fault Comm WD Time" appear in a MBTCPComm control module.
It's a CI867 under a AC 800M controller in a 800xA 5.0 SP2 RevD.
Do you know how to restablish it?
Regards,
Marco
Answers
Hello,
just sharing... It was a communication failure due to the time difference between control network and the Modbus slave system.
After fixing the time issue and reseting the slave, variables were back.
Regards,
Marco
by backdraft