Error in Calling graphics aspect
It is in operator station. and not able to edit on that stations.
Can i erase FSDCHACHE in OperateITTemp Folder of that stations.
E_AFW_CS_TIMEOUT coming.
Please help.
Voted best answer
Hi
Some checkpoints:
- Do the node has all System extensions installed.
- Is the problem repeated for all Graphic Elements or some..
- If all the system extensions are installed, then try removing the client and adding it using Configuration Wizard.
One suggestion, kindly provide the details of the problem, system version details it will help all readers to understand the problem
Best Regards
Sunny Khatri
Answers
The timeout seems odd.
Does the same graphic aspect open properly on other machines?
The OperateITTemp folder's contents can be deleted if the workplaces, tools (Control Builder M, Graphics Builder), etc. are closed first. The contents of the OperateITTemp folder will be rebuilt as necessary, also the FSDCache.
/Stefan
Dear Mr Sunil Khatri
Sir it was a a working Node(Operator stations).
Suddenly this problem started.
Our system is 800xa4.1.
After this problem we restore the image backup which we do take at regular interval.
But still we are facing the same problem.
Dear Mr Stefan Strömqvist
Yes same graphics is opening in other staions perfectly.
Verify that the malfunctioning client does not become blocked by some affinity rule.
Its indeed possible to prevent a certain client from reaching a particular service by adding the client to affinity, but not any server to that client row.
If affinity is enable, try disabling it for e.g. FSD and see if there is a difference.